iBoot DC Relay Specs

iBoot DC Relay Specs

Postby andrewm » May 13th, 2014, 11:37 pm

I am using an iBoot DC to control the DC Power to an Advantech PC UNO-2173AF.
I previously used a relay set from ControlAnything and had an issue with relay bounce. The switched rail would take > 20 ms to settle, and the PCs would intermittently fail to start.
I designed a circuit to clean this up using a delay and a semiconductor switch.
I have measured the settling time on one iBoot DC and it came in around 7 ms.

My question is am I going to be able to drop the semiconductor cleanup circuit?
OR really, do you have any specs on the relay used in the iBoot DC??
andrewm
 
Posts: 2
Joined: May 12th, 2014, 8:00 pm

Re: iBoot DC Relay Specs

Postby DP_Sam » May 15th, 2014, 1:35 pm

Andrew,

I can not tell if you can remove the cleanup circuit. My guess is probably.
This link is the data sheet for the relay inside the unit.
How long have you had the iBoot-DC? What is the Serial number?
Sam Savoye
Dataprobe Tech Support
SSavoye@Dataprobe.com
DP_Sam
 
Posts: 123
Joined: January 21st, 2010, 9:39 am
Location: Allendale, NJ

Re: iBoot DC Relay Specs

Postby andrewm » May 20th, 2014, 3:17 am

DP_Sam,

Thanx for the response. I bought the iBoot DC in Australia - ordered it on 2nd April.
It is in the field at the moment, so I don't have the serial number, but I can get it.
I have three more on order, and intend to just test them on a couple of the PCs.

I note the spec says 20 ms (MAX) operate, which is a bit more than I measured ...
andrewm
 
Posts: 2
Joined: May 12th, 2014, 8:00 pm